Joe Nuciforo Jr.
5/8/2015
 Moisture content of substrate
 Continuity of materials in the makeup of the
concrete
 Thickness of nonconductive lining
 Voltage level
 DC constant or DC pulse
 Moisture content is directly related to the dielectric value
of the concrete substrate. The DC voltage of high voltage
testing units use the continuity of the moisture in the
concrete to complete the circuit and identify the
discontinuity's in a non conductive coating system. If the
concrete has a low moisture content(0 to 3 %) the high
voltage test will be inconclusive at best. A moisture
content of 3% to 7% is better. A moisture content od 7% to
12% is optimal . Moisture contents over 12% can inhibit
the resin migration of a topical coating and produce a
lower bond strength.
 Throughout the United States we have a wide variety of
climate zones with varying relative humidity and soil
moisture contents. With buried concrete structures. These
soil moisture contents play a key role in hydration of the
concrete and the effectiveness and accuracy of the high
voltage test being performed. For concrete structures
above ground relative humidity plays the most important
role for hydration of the concrete because of the porous
nature of concrete it will absorb and retain moisture and
keep a fairly steady moisture content relative to the
atmospheric humidity.
 Where this is most affected is in the Southwest United
States do to low atmospheric humidity and deep ground
water tables. Stable conditions around buried concrete
structures that have been in place for more than 2 months
will have an equalized moisture content matching the soils
around it with normal transpiration . Newly excavated
soils will has an inconsistent moisture content do to the
fact that normal movement of moisture thru transpiration
has not been reestablished . This is most prevalent in new
construction. A waiting period after installation of the
concrete structures and back fill of the sub grade materials
should be observed (2 months) so the moisture contents
can stabilize.
 Case point: Sierra Morado sub division.
 In the first two weeks of November 2014, 18 new
construction manholes were coated and tested prior to
back fill and topical treatment (asphalt) . High voltage
tests were done on all manholes and discontinuity's were
repaired. Manholes were retested and no further
discontinuity's were found . The municipality’s
representative was present for a final high voltage test and
no discontinuity's were found.
 In the last 2 weeks of March 2015 the topical treatments
were complete and the contractor was called in to patch
the adjustment rings. Asphalt had been down 3 weeks.
Upon completion of the patching ,the adjustments were
tested and patched. A field superintendent retested one of
the previously tested and passed manhole completely and
found discontinuity's throughout . All manholes were
retested and found to have 30% to 50% more previously
unidentified discontinuity's . This is believed to be do to
the raised moisture content and increased dielectric value
of the substrate concrete.
 Instrument used to test moisture contents Delmhorst BD-
7 serial # 008167
 Usually the materials that concrete are
comprised of has a very low dielectric value.
Random materials usually in the aggregate have
a higher than normal dielectric value. For
instance a piece of aggregate with a high iron
content will be more conductive than a piece of
quartz. This is a very rare thing that should not
greatly affect the out come of a high voltage
spark test. Test Equipment that will give you a
dielectric value of the concrete substrate should
be used to verify the value. One such piece of
equipment is a Prostat PRS-801 Resistance
system. These units will cost approximately
$2500 to $3000 dollars. As you test the substrate
you will notice a variation in values from one
location to another ( sometimes as small as 2
inches difference). You will also see variations in
values from vertical to horizontal .
 Horizontal surfaces have a much more
consistent values do to much more consistent
moisture contents.
 Vertical surfaces have many more variable like
back fill of soil around the opposite side ,
moisture content of the soil, transpiration rates
of the soil, free standing walls that have a very
low moisture content do to evaporation.
 The thickness of a no conductive
coating is a very important factor in
your high voltage test. The high
voltage test unit has a set voltage for
each thickness of coating/lining. If
the voltage used is insufficient to
jump the distance of the coating
thickness (spark over) you will not
get a valid test. Irregularity's in
substrate and over application of
products can impact the test results.
It is always wise to do adhesion
tests (D-7234-05) along with spark
testing of new coatings. After the
adhesion test are complete, check
the profile of the puck removed
from the adhesion test to verify
thickness of coating for proper
voltage selection.
 The voltage selection is important to
the accuracy of the test results. If
voltage is to low you will not be able
to achieve the proper spark over. If
voltage is to high you will get
incorrect voltage back to your high
voltage test unit and an audible
alarm will sound with no
identifiable discontinuity. This is
also true when the coating/ lining is
to thin . The high voltage test unit
will sense greater than expected
voltage return and will sound the
audible alarm with no discontinuity
and at proper voltage for specified
thickness.
CONCRETE STEEL
 We used one Tinker and Rasor APW-
GSE pulse high voltage test unit 1298 ,
one Tinker and Rasor AP/W pulse
high voltage test unit13436 and one
Elcometer T26620033-3 direct voltage
tester HKA934 to test a liner at 170
mills on concrete. Both the APW-GSE
and the Elcometer T26620033-3 high
voltage testers worked well and picked
up all the discontinuity's but two do to
the lack of moisture in the concrete
substrate making it hard to determine
accuracy of the test. Each unit picked
up two different discontinuity's that
the other would not. This makes it
impossible for me to say whether one
system works better than the other.
Both the APW-GSE and the T26620033-
3 ricked up 30% more discontinuity's
than the older AP/W unit 13436
 We used one Tinker and Rasor
APW-GSE pulse high voltage test
unit 1298 , one Tinker and Rasor
AP/W pulse high voltage test unit
13436 and one Elcometer
T26620033-3 direct voltage tester
HKA934 to test lining at 85 mills
on steel. All three test units
performed identical. This leads
me to believe that that the
substrate continuity of concrete
for identifying discontinuity's
plays a key role in the accuracy of
the test results.

More Related Content

What's hot

Rebound hammer test - Maintenance and Rehabilitation of Structures
Rebound hammer test - Maintenance and Rehabilitation of StructuresRebound hammer test - Maintenance and Rehabilitation of Structures
Rebound hammer test - Maintenance and Rehabilitation of StructuresAshishVivekSukh
 
Non destructive test in concrete in building construction architecture
Non destructive test in concrete in building construction architectureNon destructive test in concrete in building construction architecture
Non destructive test in concrete in building construction architectureAditya Sanyal
 
Rheology of concrete
Rheology of concreteRheology of concrete
Rheology of concreteajay nagaraj
 
Ce8611 Highway Engineering Laboratory Manual
Ce8611 Highway Engineering Laboratory ManualCe8611 Highway Engineering Laboratory Manual
Ce8611 Highway Engineering Laboratory ManualLokesh Kalliz
 
Concrete Technology
Concrete TechnologyConcrete Technology
Concrete TechnologyLove Sharma
 
Testing of dry/hardened concrete
Testing of dry/hardened concreteTesting of dry/hardened concrete
Testing of dry/hardened concreteE. O. Ochieng'
 
Compacting Factor Test
Compacting Factor TestCompacting Factor Test
Compacting Factor TestXinYee Khoo
 
Construction Testing Cement Testing
Construction Testing  Cement TestingConstruction Testing  Cement Testing
Construction Testing Cement TestingShambhudayal
 
Vebe test for workability of fresh concrete
Vebe test for workability of fresh concreteVebe test for workability of fresh concrete
Vebe test for workability of fresh concreteMuhammad Saleem
 
TESTING OF CEMENT IN LABORATORY
TESTING OF CEMENT IN LABORATORYTESTING OF CEMENT IN LABORATORY
TESTING OF CEMENT IN LABORATORYpwhite91
 
workability test of concrete
workability test of concreteworkability test of concrete
workability test of concreteKaran Patel
 
Tests on cement
Tests on cementTests on cement
Tests on cementDeviprasad
 

What's hot (20)

Hardened concrete
Hardened concreteHardened concrete
Hardened concrete
 
Rebound hammer test - Maintenance and Rehabilitation of Structures
Rebound hammer test - Maintenance and Rehabilitation of StructuresRebound hammer test - Maintenance and Rehabilitation of Structures
Rebound hammer test - Maintenance and Rehabilitation of Structures
 
Non destructive test in concrete in building construction architecture
Non destructive test in concrete in building construction architectureNon destructive test in concrete in building construction architecture
Non destructive test in concrete in building construction architecture
 
Rheology of concrete
Rheology of concreteRheology of concrete
Rheology of concrete
 
Ce8611 Highway Engineering Laboratory Manual
Ce8611 Highway Engineering Laboratory ManualCe8611 Highway Engineering Laboratory Manual
Ce8611 Highway Engineering Laboratory Manual
 
Concrete Technology
Concrete TechnologyConcrete Technology
Concrete Technology
 
Testing of dry/hardened concrete
Testing of dry/hardened concreteTesting of dry/hardened concrete
Testing of dry/hardened concrete
 
Cement tests
Cement testsCement tests
Cement tests
 
Compacting Factor Test
Compacting Factor TestCompacting Factor Test
Compacting Factor Test
 
Ndt
NdtNdt
Ndt
 
Construction Testing Cement Testing
Construction Testing  Cement TestingConstruction Testing  Cement Testing
Construction Testing Cement Testing
 
Properties of concrete
Properties of concrete Properties of concrete
Properties of concrete
 
Vebe test for workability of fresh concrete
Vebe test for workability of fresh concreteVebe test for workability of fresh concrete
Vebe test for workability of fresh concrete
 
TESTING OF CEMENT IN LABORATORY
TESTING OF CEMENT IN LABORATORYTESTING OF CEMENT IN LABORATORY
TESTING OF CEMENT IN LABORATORY
 
Timmareddy
TimmareddyTimmareddy
Timmareddy
 
workability test of concrete
workability test of concreteworkability test of concrete
workability test of concrete
 
Tests on cement
Tests on cementTests on cement
Tests on cement
 
Fresh Concrete
Fresh Concrete Fresh Concrete
Fresh Concrete
 
Concrete technology
Concrete technologyConcrete technology
Concrete technology
 
Slump test
Slump testSlump test
Slump test
 

Viewers also liked

Rpp revisi 2016 biologi xii rpp diva pendidikan
Rpp revisi 2016 biologi xii  rpp diva pendidikanRpp revisi 2016 biologi xii  rpp diva pendidikan
Rpp revisi 2016 biologi xii rpp diva pendidikanDiva Pendidikan
 
Sushil Shinde - Copy
Sushil Shinde - CopySushil Shinde - Copy
Sushil Shinde - CopyAkshit Shah
 
Rpp revisi 2016 sejarah wajib xi rpp diva pendidikan
Rpp revisi 2016 sejarah wajib xi  rpp diva pendidikanRpp revisi 2016 sejarah wajib xi  rpp diva pendidikan
Rpp revisi 2016 sejarah wajib xi rpp diva pendidikanDiva Pendidikan
 
She is ATLANTA'S TopStylist
She is ATLANTA'S TopStylistShe is ATLANTA'S TopStylist
She is ATLANTA'S TopStylistleandreia
 
Good carbohydrates vs Bad carbohydrates
Good carbohydrates vs Bad carbohydrates  Good carbohydrates vs Bad carbohydrates
Good carbohydrates vs Bad carbohydrates Just for Hearts
 
Rpp revisi 2016 seni budaya seni musik x -rpp diva pendidikan
Rpp revisi 2016 seni budaya   seni musik x -rpp diva pendidikanRpp revisi 2016 seni budaya   seni musik x -rpp diva pendidikan
Rpp revisi 2016 seni budaya seni musik x -rpp diva pendidikanDiva Pendidikan
 
Rpp ktsp perjalanan bisnis xii smk rpp diva pendidikan
Rpp ktsp perjalanan bisnis xii smk   rpp diva pendidikanRpp ktsp perjalanan bisnis xii smk   rpp diva pendidikan
Rpp ktsp perjalanan bisnis xii smk rpp diva pendidikanDiva Pendidikan
 
formulario de calculo integral y diferencial
formulario de calculo integral y diferencialformulario de calculo integral y diferencial
formulario de calculo integral y diferencialKarina Lizbeth
 
OppMax Blogs by Katie Binkholder
OppMax Blogs by Katie BinkholderOppMax Blogs by Katie Binkholder
OppMax Blogs by Katie BinkholderKatie Binkholder
 
Kern process heat transfer
Kern   process heat transferKern   process heat transfer
Kern process heat transferDilip Kumar
 

Viewers also liked (12)

St emgoldex
St emgoldexSt emgoldex
St emgoldex
 
Rpp revisi 2016 biologi xii rpp diva pendidikan
Rpp revisi 2016 biologi xii  rpp diva pendidikanRpp revisi 2016 biologi xii  rpp diva pendidikan
Rpp revisi 2016 biologi xii rpp diva pendidikan
 
Sushil Shinde - Copy
Sushil Shinde - CopySushil Shinde - Copy
Sushil Shinde - Copy
 
Rpp revisi 2016 sejarah wajib xi rpp diva pendidikan
Rpp revisi 2016 sejarah wajib xi  rpp diva pendidikanRpp revisi 2016 sejarah wajib xi  rpp diva pendidikan
Rpp revisi 2016 sejarah wajib xi rpp diva pendidikan
 
She is ATLANTA'S TopStylist
She is ATLANTA'S TopStylistShe is ATLANTA'S TopStylist
She is ATLANTA'S TopStylist
 
Good carbohydrates vs Bad carbohydrates
Good carbohydrates vs Bad carbohydrates  Good carbohydrates vs Bad carbohydrates
Good carbohydrates vs Bad carbohydrates
 
Rpp revisi 2016 seni budaya seni musik x -rpp diva pendidikan
Rpp revisi 2016 seni budaya   seni musik x -rpp diva pendidikanRpp revisi 2016 seni budaya   seni musik x -rpp diva pendidikan
Rpp revisi 2016 seni budaya seni musik x -rpp diva pendidikan
 
Rpp ktsp perjalanan bisnis xii smk rpp diva pendidikan
Rpp ktsp perjalanan bisnis xii smk   rpp diva pendidikanRpp ktsp perjalanan bisnis xii smk   rpp diva pendidikan
Rpp ktsp perjalanan bisnis xii smk rpp diva pendidikan
 
Webcam
WebcamWebcam
Webcam
 
formulario de calculo integral y diferencial
formulario de calculo integral y diferencialformulario de calculo integral y diferencial
formulario de calculo integral y diferencial
 
OppMax Blogs by Katie Binkholder
OppMax Blogs by Katie BinkholderOppMax Blogs by Katie Binkholder
OppMax Blogs by Katie Binkholder
 
Kern process heat transfer
Kern   process heat transferKern   process heat transfer
Kern process heat transfer
 

Similar to In’s and Out’s of High Voltage Spark Testing

Principles & Testing Methods Of Earth Ground Resistance
Principles & Testing Methods Of Earth Ground ResistancePrinciples & Testing Methods Of Earth Ground Resistance
Principles & Testing Methods Of Earth Ground ResistancePower System Operation
 
Electronic devices used in reinforced concrete by eng mustafa
Electronic devices used in reinforced concrete by eng mustafaElectronic devices used in reinforced concrete by eng mustafa
Electronic devices used in reinforced concrete by eng mustafamustafa abdulwahed
 
Fast electrode profile
Fast electrode profileFast electrode profile
Fast electrode profilesachindesai055
 
Fresh concrete properties & its standard tests
Fresh concrete properties & its standard testsFresh concrete properties & its standard tests
Fresh concrete properties & its standard testsMaHmoud AliraQi
 
Sarvayogam corp presentation on chemical earthing
Sarvayogam corp  presentation on chemical earthingSarvayogam corp  presentation on chemical earthing
Sarvayogam corp presentation on chemical earthingShrikant Iyer
 
IRJET - Experimental Study on Effect of Magnetized Water in Concrete Mix
IRJET - Experimental Study on Effect of Magnetized Water in Concrete MixIRJET - Experimental Study on Effect of Magnetized Water in Concrete Mix
IRJET - Experimental Study on Effect of Magnetized Water in Concrete MixIRJET Journal
 
Wael Abdel-Rahman Mohamed Ahmed_Grounding_lecture(L5).ppt
Wael Abdel-Rahman Mohamed Ahmed_Grounding_lecture(L5).pptWael Abdel-Rahman Mohamed Ahmed_Grounding_lecture(L5).ppt
Wael Abdel-Rahman Mohamed Ahmed_Grounding_lecture(L5).pptDKChaitanyarajSingh
 
Condition survey and nde
Condition survey and ndeCondition survey and nde
Condition survey and ndeJay Bhavsar
 
Non destructive test (ndt) on concrete msu
Non destructive test (ndt) on concrete msuNon destructive test (ndt) on concrete msu
Non destructive test (ndt) on concrete msuSagar Vekariya
 
UNIT 5 PART 2.pptx
UNIT 5 PART 2.pptxUNIT 5 PART 2.pptx
UNIT 5 PART 2.pptxSHRUTHIBS16
 
Soil Test and Surveys
Soil Test and SurveysSoil Test and Surveys
Soil Test and SurveysJerome Jaime
 

Similar to In’s and Out’s of High Voltage Spark Testing (20)

Grounding1
Grounding1Grounding1
Grounding1
 
Principles & Testing Methods Of Earth Ground Resistance
Principles & Testing Methods Of Earth Ground ResistancePrinciples & Testing Methods Of Earth Ground Resistance
Principles & Testing Methods Of Earth Ground Resistance
 
Electronic devices used in reinforced concrete by eng mustafa
Electronic devices used in reinforced concrete by eng mustafaElectronic devices used in reinforced concrete by eng mustafa
Electronic devices used in reinforced concrete by eng mustafa
 
Fast electrode profile
Fast electrode profileFast electrode profile
Fast electrode profile
 
Slump Test - Report
Slump Test - ReportSlump Test - Report
Slump Test - Report
 
Fresh concrete properties & its standard tests
Fresh concrete properties & its standard testsFresh concrete properties & its standard tests
Fresh concrete properties & its standard tests
 
Earthings
EarthingsEarthings
Earthings
 
Sarvayogam corp presentation on chemical earthing
Sarvayogam corp  presentation on chemical earthingSarvayogam corp  presentation on chemical earthing
Sarvayogam corp presentation on chemical earthing
 
IRJET - Experimental Study on Effect of Magnetized Water in Concrete Mix
IRJET - Experimental Study on Effect of Magnetized Water in Concrete MixIRJET - Experimental Study on Effect of Magnetized Water in Concrete Mix
IRJET - Experimental Study on Effect of Magnetized Water in Concrete Mix
 
Wael Abdel-Rahman Mohamed Ahmed_Grounding_lecture(L5).ppt
Wael Abdel-Rahman Mohamed Ahmed_Grounding_lecture(L5).pptWael Abdel-Rahman Mohamed Ahmed_Grounding_lecture(L5).ppt
Wael Abdel-Rahman Mohamed Ahmed_Grounding_lecture(L5).ppt
 
Grounding.ppt
Grounding.pptGrounding.ppt
Grounding.ppt
 
Properties of concrete
Properties of concrete Properties of concrete
Properties of concrete
 
ملزمة
ملزمةملزمة
ملزمة
 
Condition survey and nde
Condition survey and ndeCondition survey and nde
Condition survey and nde
 
Non destructive test (ndt) on concrete msu
Non destructive test (ndt) on concrete msuNon destructive test (ndt) on concrete msu
Non destructive test (ndt) on concrete msu
 
UNIT 5 PART 2.pptx
UNIT 5 PART 2.pptxUNIT 5 PART 2.pptx
UNIT 5 PART 2.pptx
 
Soil Test and Surveys
Soil Test and SurveysSoil Test and Surveys
Soil Test and Surveys
 
Test of concrete
Test of concrete Test of concrete
Test of concrete
 
Edangal - Journal
Edangal - JournalEdangal - Journal
Edangal - Journal
 
Techshore Inspection Services-Concrete NDT.pdf
Techshore Inspection Services-Concrete NDT.pdfTechshore Inspection Services-Concrete NDT.pdf
Techshore Inspection Services-Concrete NDT.pdf
 

In’s and Out’s of High Voltage Spark Testing

  • 2.  Moisture content of substrate  Continuity of materials in the makeup of the concrete  Thickness of nonconductive lining  Voltage level  DC constant or DC pulse
  • 3.  Moisture content is directly related to the dielectric value of the concrete substrate. The DC voltage of high voltage testing units use the continuity of the moisture in the concrete to complete the circuit and identify the discontinuity's in a non conductive coating system. If the concrete has a low moisture content(0 to 3 %) the high voltage test will be inconclusive at best. A moisture content of 3% to 7% is better. A moisture content od 7% to 12% is optimal . Moisture contents over 12% can inhibit the resin migration of a topical coating and produce a lower bond strength.  Throughout the United States we have a wide variety of climate zones with varying relative humidity and soil moisture contents. With buried concrete structures. These soil moisture contents play a key role in hydration of the concrete and the effectiveness and accuracy of the high voltage test being performed. For concrete structures above ground relative humidity plays the most important role for hydration of the concrete because of the porous nature of concrete it will absorb and retain moisture and keep a fairly steady moisture content relative to the atmospheric humidity.  Where this is most affected is in the Southwest United States do to low atmospheric humidity and deep ground water tables. Stable conditions around buried concrete structures that have been in place for more than 2 months will have an equalized moisture content matching the soils around it with normal transpiration . Newly excavated soils will has an inconsistent moisture content do to the fact that normal movement of moisture thru transpiration has not been reestablished . This is most prevalent in new construction. A waiting period after installation of the concrete structures and back fill of the sub grade materials should be observed (2 months) so the moisture contents can stabilize.  Case point: Sierra Morado sub division.  In the first two weeks of November 2014, 18 new construction manholes were coated and tested prior to back fill and topical treatment (asphalt) . High voltage tests were done on all manholes and discontinuity's were repaired. Manholes were retested and no further discontinuity's were found . The municipality’s representative was present for a final high voltage test and no discontinuity's were found.  In the last 2 weeks of March 2015 the topical treatments were complete and the contractor was called in to patch the adjustment rings. Asphalt had been down 3 weeks. Upon completion of the patching ,the adjustments were tested and patched. A field superintendent retested one of the previously tested and passed manhole completely and found discontinuity's throughout . All manholes were retested and found to have 30% to 50% more previously unidentified discontinuity's . This is believed to be do to the raised moisture content and increased dielectric value of the substrate concrete.  Instrument used to test moisture contents Delmhorst BD- 7 serial # 008167
  • 4.  Usually the materials that concrete are comprised of has a very low dielectric value. Random materials usually in the aggregate have a higher than normal dielectric value. For instance a piece of aggregate with a high iron content will be more conductive than a piece of quartz. This is a very rare thing that should not greatly affect the out come of a high voltage spark test. Test Equipment that will give you a dielectric value of the concrete substrate should be used to verify the value. One such piece of equipment is a Prostat PRS-801 Resistance system. These units will cost approximately $2500 to $3000 dollars. As you test the substrate you will notice a variation in values from one location to another ( sometimes as small as 2 inches difference). You will also see variations in values from vertical to horizontal .  Horizontal surfaces have a much more consistent values do to much more consistent moisture contents.  Vertical surfaces have many more variable like back fill of soil around the opposite side , moisture content of the soil, transpiration rates of the soil, free standing walls that have a very low moisture content do to evaporation.
  • 5.  The thickness of a no conductive coating is a very important factor in your high voltage test. The high voltage test unit has a set voltage for each thickness of coating/lining. If the voltage used is insufficient to jump the distance of the coating thickness (spark over) you will not get a valid test. Irregularity's in substrate and over application of products can impact the test results. It is always wise to do adhesion tests (D-7234-05) along with spark testing of new coatings. After the adhesion test are complete, check the profile of the puck removed from the adhesion test to verify thickness of coating for proper voltage selection.  The voltage selection is important to the accuracy of the test results. If voltage is to low you will not be able to achieve the proper spark over. If voltage is to high you will get incorrect voltage back to your high voltage test unit and an audible alarm will sound with no identifiable discontinuity. This is also true when the coating/ lining is to thin . The high voltage test unit will sense greater than expected voltage return and will sound the audible alarm with no discontinuity and at proper voltage for specified thickness.
  • 6. CONCRETE STEEL  We used one Tinker and Rasor APW- GSE pulse high voltage test unit 1298 , one Tinker and Rasor AP/W pulse high voltage test unit13436 and one Elcometer T26620033-3 direct voltage tester HKA934 to test a liner at 170 mills on concrete. Both the APW-GSE and the Elcometer T26620033-3 high voltage testers worked well and picked up all the discontinuity's but two do to the lack of moisture in the concrete substrate making it hard to determine accuracy of the test. Each unit picked up two different discontinuity's that the other would not. This makes it impossible for me to say whether one system works better than the other. Both the APW-GSE and the T26620033- 3 ricked up 30% more discontinuity's than the older AP/W unit 13436  We used one Tinker and Rasor APW-GSE pulse high voltage test unit 1298 , one Tinker and Rasor AP/W pulse high voltage test unit 13436 and one Elcometer T26620033-3 direct voltage tester HKA934 to test lining at 85 mills on steel. All three test units performed identical. This leads me to believe that that the substrate continuity of concrete for identifying discontinuity's plays a key role in the accuracy of the test results.